Group: DynoMotion Message: 13336 From: tapiolarikka Date: 6/10/2016
Subject: Mach3 lathe threading
On my continuous quest to cut production time I changed the the pullout/retract move to G2 that ends to starting point of next thread pass.
This resulted in the delay changing place and the machine waited at pass start. Also the last pass looked like it lauched quicker.
I just noticed that changing the windows buffer time from 3 seconds to 0.3  shortens the delay remarkably.
0.1 sec buffer time results in buffer starvation where as 30 sec buffer time has same delay as 3 seconds.
Does/can the plugin buffer threading passes in order to speed up the process?
I have v4.33 installed
Rgds,
Tapio
Group: DynoMotion Message: 13337 From: Tom Kerekes Date: 6/10/2016
Subject: Re: Mach3 lathe threading
Hi Tapio,
Can you post a GCode fragment that demonstrates the delay and all your Trajectory Planner settings?
On Jun 10, 2016, at 1:42 AM, tapio.larikka@... [DynoMotion] <DynoMotion@yahoogroups.com> wrote:
Rgds,
Tapio
Group: DynoMotion Message: 13338 From: tapiolarikka Date: 6/10/2016
Attachments :
Attached please find the Gcode.
TP settings
Mach is to 200 lines lookahead but I've never found any other TP settings with mach3.
Rgds,
Tapio
  @@attachment@@
Group: DynoMotion Message: 13339 From: Tom Kerekes Date: 6/10/2016
Subject: Re: Mach3 lathe threading [1 Attachment]
Hi Tapio,
I forgot you were using Mach3 :{
I was hoping for a smaller code fragment that I could understand without Tool changes and extra motions and such.
Is this plot (see attached) what yours looks like?  Wouldn't the G2 arc be on the wrong side into the part?
My simulation runs in 44 sec regardless of the buffer time?  What does your take?
Actually I don't understand why the Arc motion happens fairly quickly (~ 1 sec) where I was expecting moving ~15mm at 5mm/min would take 3 minutes??
TP settings
Rgds,
Tapio
Group: DynoMotion Message: 13340 From: Tapio Larikka Date: 6/10/2016
Attachments :
Yes my G2 arcs are other way around. This has to do with Mach3 "arcs reversed in front tool post"
Arc should be under the threading pass
Extra motions, namely the the Y-axis moves are for tool position changes since it is a gang tool lathe.
My Mach Elapse time Dro says 46 sec (occasionally -07:-30) or something else equally absurd), true stopwatch app. 38 sec
Arc is fast because of G95-feed per rev = 5mmx1000rpm = rapid move
I reattach the Gcode, I edited out all toolchanges, Y-moves and system specific Mcodes. I also changed the G2's to G3 so that thay should be correct in your system.
After my previous post I made two videos of the workcycle with both buffer settings.
Unfortunatelly the videos were taken with samsung S7, resulting to 60MB files that I can't upload to group/Files/my folder because of the 10MB limit.
For some odd samusung reason the picture is also sideways.
Also noticed that my XP pc with intel celeron can't play back smoothly so atleast on my screen the delay is not as clear as in real world.
Is there anywhere else I could upload them?
Group: DynoMotion Message: 13341 From: Tom Kerekes Date: 6/10/2016
Hi Tapio,
Thanks.  That is simpler and looks correct.  But I still don't see an abnormal delay.  Mine runs in 14 seconds regardless of the Buffering.
Consider uploading to Youtube.  They are pretty good about handling and fixing most formats.
Group: DynoMotion Message: 13342 From: Tapio Larikka Date: 6/11/2016
Attachments :
    Windows buffer time 3 seconds:  https://youtu.be/uGlA17TFJV4
    Windows buffer time 0.4 seconds: https://youtu.be/WifaMpSrTb4
    Please excuse the instability in 3 sec video, caused by chip hitting the camera man in the face.
    I tested running in simulation and it does not show same delay as in real world.
    From what I have read on various posts this delay in threading is present with most external controllers,
    this threading with mach/Galil: https://www.youtube.com/watch?v=JfnQxDPWoEQ being only exception I have found
    Threading starts at 1:38
    I usually use G76 macro for threading, for the ease of tweaking the measurements when needed, but several cross checks show no difference in time/delay,
    so the delay is not due to mach3 macro handling.
    Tapio
    Group: DynoMotion Message: 13344 From: Steve Blackmore Date: 6/12/2016
    Comparing apples to oranges there I think, the Galil uses Ethernet, not
    USB so buffer refresh rates are considerably quicker.
    Try it with G32 not macro.
    Mach3 as with most other controls uses the index pulse as the timer for
    the start of the threading pass. It waits for the next pulse before
    issuing the next line. (From discussions a while ago and a fading
    memory- that might actually be two or three pulses to ensure no false
    trigger).
    The thread pitch, diameter, spindle speed and lead in distance all
    affect the delay to some degree also.
    Looking at your videos that looks normal for a USB control with Mach.
    Steve Blackmore
    Group: DynoMotion Message: 13350 From: Tom Kerekes Date: 6/12/2016
    Hi Steve/Tapio,
    I think the Galil might be a pci/isa card actually.
    Tapio is using G32 and said it behaves no different from G76
    I shouldn't have said I was "simulating".  The test setup is actually moving/driving motors on the bench.  I just don't have a real Lathe connected.  So the timing should be real.
    Actually with our Plugin an A/B quadrature encoder signal is used not an index pulse.  But regardless there will be a fraction of one rotation delay to sync to the Spindle angle for each pass.  But at 1000RPM that should be less than 60ms.
    I did some investigation and wrote a KFLOP C Program to monitor and time the start/stops of coordinated motion to measure the amount of dead time.  See attached.  There is a small difference with regard to the buffering (we could probably address that if necessary).   But the main delay seems to come from Mach3.  It only calls the plugin 10X per second (~100ms each).  When one pass or motion ends and we tell Mach3 everything is complete until Mach3 starts giving new motion data there are about 3~4 calls with no data.  That results in a few 200~300ms delay deltas shown below.  I don't know what Mach3 is waiting for.  Ironically a bug inadvertently introduced that hogged a lot of time in our Plugin caused the times to go down  somewhat, but that caused other problems such as the Mach3 GUI didn't update.
    Mach3 (0.3 sec buffering)
    Start = 0.000000ms Delta = 0.000000ms Total = 0.000000 Indx=5
    Start = 1094.041720ms Delta = 804.068140ms Total = 804.068140 Indx=1
    Start = 2631.871700ms Delta = 537.756480ms Total = 1341.824620 Indx=12
    Start = 3505.052300ms Delta = 259.206660ms Total = 1601.031280 Indx=5
    Start = 5260.591660ms Delta = 255.425660ms Total = 1856.456940 Indx=5
    Start = 7000.471740ms Delta = 277.296140ms Total = 2133.753080 Indx=5
    Start = 8748.181720ms Delta = 302.946200ms Total = 2436.699280 Indx=5
    Start = 10498.861540ms Delta = 269.732080ms Total = 2706.431360 Indx=5
    Start = 11595.601440ms Delta = 316.445820ms Total = 3022.877180 Indx=5
    Here is KMotionCNC running the same sequence (3.0 sec buffering)
    Start = 0.000000ms Delta = 0.000000ms Total = 0.000000 Indx=6
    Start = 570.692300ms Delta = 383.048120ms Total = 383.048120 Indx=21
    Start = 1091.252500ms Delta = 28.897000ms Total = 411.945120 Indx=3
    Start = 1936.351640ms Delta = 81.816000ms Total = 493.761120 Indx=124
    Start = 2398.052420ms Delta = 26.737000ms Total = 520.498120 Indx=3
    Start = 3244.501640ms Delta = 74.525900ms Total = 595.024020 Indx=122
    Start = 3711.601980ms Delta = 26.462880ms Total = 621.486900 Indx=3
    Start = 4564.801540ms Delta = 79.111740ms Total = 700.598640 Indx=122
    Start = 5027.582000ms Delta = 17.282980ms Total = 717.881620 Indx=3
    Start = 5884.021620ms Delta = 81.542300ms Total = 799.423920 Indx=122
    Start = 6348.692420ms Delta = 14.586940ms Total = 814.010860 Indx=3
    Start = 7128.721700ms Delta = 8.911900ms Total = 822.922760 Indx=4
    Can we convince you to switch to KMotionCNC? It looks as if there would be a significant time savings.
    trigger).
    Steve Blackmore
      @@attachment@@
    Group: DynoMotion Message: 13352 From: bennyattwell Date: 6/13/2016
    i have all the data here for the mach3 / galil threading
    the video shown was done with an ethernet controller.
    it uses plugin notifies to pass all required data to the galil.
    the galil handles all threading in a thread- with a program burnt into that thread
    when complete it hands control back to mach3
    i have the mach macro and the .dmc threading program if its of any use.
    the .dmc program does all calculations for tapers etc etc
    i know ken crouch  spent years programming this to get it all to work as it does
    annoyingly i still havnt found the time to implement it into my lathe.
    Group: DynoMotion Message: 13353 From: Tapio Larikka Date: 6/13/2016
    Hi Tom,Steve&Brandon (thanks for chiming in)
    I have used both G32 and G76, main idea for trying G32 was to see if G76 macro increases the delay due to the macro interpretation.
    To my understanding macros handle the movement commads as if the were input to MDI on line by line basis.
    Since I could not detect any difference I now use G76 as it is easier to change measurements or number of passes as needed.
    There may well be measurable difference in millisec but none to human eye.
    Yes, when simulating means moving motors then the delay should be visible
    To my understanding common to all motion plugins is that mach3 expects the plugin to handle whole threading operation, just sits and waits for ready info.
    I have understood that mach outputs linear and arc moves as stream of setpoints and corresponding time to get there, basically inverse time mode, but that threading is different.
    I found it interesting that threading pass and pullout/retract move stay as continuous move regardless of the type/shape they are:
    G1, G2 as half circle at X-pullout distance, or G2 from endpoint of pass to starting point of next pass.
    What would happen if you told Mach that threading is complete right after its processed and sent to Kflop? Is it possible to buffer the threading passes?
    How far rigid tapping (NotifyMachTap) would be from the approach Brandon said Galil uses?
    I have been convinced to switch to KMotionCNC for a while already. I'm just stuck with Mach for the time being because:
    My lathe setup is gang tool so I need the Y-axis and A-axis is used for spindle indexing needed to lock/unlock the 5C collet based chuck you see on my video.
    Partscounter/autorepeat work cycle/run till ref qty
    G-code macro generation
    I could work around first two with user programs,  but last one needs mach style screen editor with scripting or .net based front end.
    Judging by my current progress with vb.net I guess I'm ready sometime next decade :(
    Rgds,
    Tapio
    Group: DynoMotion Message: 13354 From: Tom Kerekes Date: 6/13/2016
    Hi Tapio,
    Basically Yes.  But that happens for each pass.  As well as for other motions and dwells.
    The stream of points are equally spaced in time (2ms).  Threading is not really any different except that #1 when threading starts the motion the motion should begin when the spindle is at a certain orientation and #2 the motion (pseudo  time) should be geared proportionally to the spindle motion.
    face="Arial" size="2">What would happen if you told Mach that threading is complete right after its processed and sent to Kflop? Is it possible to buffer the threading passes?
    I can't think of an easy way to do that because Mach3 expects to stop and synchronize to the machine position at the end of the sequence.  I suppose it could all be faked but this would be very complicated.
    face="Arial" size="2">How far rigid tapping (NotifyMachTap) would be from the approach Brandon said Galil uses?
    I suppose that might work.  A number of parameters much like G76 has could be passed to  KFLOP C Program.  Then the C Program could create all the coordinated motions within KFLOP and Trigger the Threading motions for the number of passes and so forth.  That way it would all happen in real-time with no delays.
    >>>> KMotionCNC
    size="2">G-code macro generation
    What are you referring to here?  Something like a Mach3 Wizard Screen?
    Rgds,
    Tapio
    Group: DynoMotion Message: 13355 From: tapiolarikka Date: 6/13/2016
    So as to simplify the problem is that where I want to make one thread in 5 passes
    Mach makes 5 threads on one part and needs 5 times more time for resyncing and peddeling around.
    I think then best solution for me would be to rewrite the G76 macro so that it passes the threading
    parameters to user program (Notify msg 10076) and the user program handles the whole threading.
    I am fairly confident on passing the parameters, but placing of commands to motion buffer and thread triggering
    is above my skillset.
    Would you happen to have an example/skeleton code?
    Wizard? - Yes, much like mach wizards, just instead of using changing to wizard screenset, I added
                       extra page to my screen, where I have DROs for parameters and buttons to generate gcode based
                      on those parameters.
    Rgds,
    Tapio
    Group: DynoMotion Message: 13356 From: Tom Kerekes Date: 6/14/2016
    Hi Tapio,
    Performing Threading from a KFLOP C Program is the same as Coordinated Motion (See the example CoordMotionInKFLOPTest.c also  attached) with the exception of instead of calling the ExecBuf() function to start the motion with constant time base, call TrigThreading(BaseSpeedRPS) that will sync to the spindle 0 degree point before starting and progress based on the spindle motion.
    Regarding the "Wizard" Screen: You could write a simple form in C# that could run as a separate App that could pop up from a KMotionCNC User button.  The App could then create a GCode File based on the form parameters, load it into KMotionCNC, and exit.   We have added a fair amount of "Automation" functionality into KMotionCNC so other Apps written in other Languages can send Messages to KMotionCNC to do things like loading a specified file.   I can provide more details if you are interested.
    Rgds,
    Tapio
      @@attachment@@
    Group: DynoMotion Message: 13358 From: Tapio Larikka Date: 6/14/2016
    I see said the blind man, or almost in my case(starting to get age vision)
    I had just figured out so much that there must be an example I can use since KMotionCNC does threading, but time and agin I fail to read through th c program files.
    Apparently everything I can ask is already there.
    CoordMotionInKFLOPTest.c:
    Coordsystem is already defined at init so this can be left out?
    VM would equal pitch in counts/sec at given BaseSpeedRPS ?
    Example places 4 moves in buffer and has one execbuf() for all of them so do I then write:
    openbuf
    VM = pitch
    linear             //threading pass 1
    VM = 3*pitch  //rapid for retract speed
    Arc                //retract move on XZ plane to the starting point of next pass
    VM = pitch
    linear             //threading pass 2
    VM = pitch
    linear             //threading pass 3
    VM = pitch
    linear             //threading pass 4
    VM = pitch
    linear             //threading pass 5
    linear             //retract move out of workpiece
    trigthread(basespeedrps)
    while (!CheckDoneBuf())
    Or does each pass need to be separated like:
    openbuf
    Example arc is on XY plane. How do I change it to XZ plane?
    I return to the wizard subject when I get so far.
    Tapio
    Group: DynoMotion Message: 13359 From: Tom Kerekes Date: 6/14/2016
    Hi Tapio,
    See below
    >>>> Correct
    >>>>> Correct
    openbuf
    VM = pitch
    VM = pitch
    VM = pitch
    VM = pitch
    VM = pitch
    openbuf
    >>>> A TrigThread(basespeedrps) is required for each pass as each pass needs to be triggered to start at the same Spindle Angle
    >>>> You would need to reconfigure the Axes in the Included routines.  I can help with that but why do you want arcs anyway?  I'd recommend just doing Independent Rapid motions which should be faster and utilize faster and smoother 3rd order motion.  I suggest:
    #1 Rapid retract in X some amount
    #2 when X moves enough begin rapid in Z
    #3 When Z gets close begin rapid back in X
    >>>> I'm not sure if you are referring to a KMotionCNC Wizard or your Mach3 "Wizard" Screen.  Assuming the Mach3 Wizard Screen - yes I would first get the multipass threading working with hard coded values, then after it is working parameterize it with your Wizard.
    Tapio
    Group: DynoMotion Message: 13360 From: Tapio Larikka Date: 6/15/2016
    Once again to see if I understood this right
    openbuf
    VM = pitch
    openbuf
    linear  X               // pullout
    linear  Z               // back to start of next pass
    linear  X               // start dept of next pass
    ExecBuf
    Above repeated by number of passes
    Some post on Mach forum I read said that Mach M calls introduce small delay because Mach flushes buffer so
    I presume there should be no conflict issues to worry about when calling openbuf from user program. (conflicts with plugin)
    I suppose user programs only have point to point moves available, no corner roundings (if not hardcoded as arcs) or continuous velocity etc.
    The arc as pullout/retract is/was to reduce jerk in Mach trapezoidal system and to cut Mach macro commands from 3 to 1 in an attempt
    to reduce the delay. I dont have means to measure the effect on axis accel but machine sounds much better
    Tapio
    Group: DynoMotion Message: 13361 From: Tom Kerekes Date: 6/15/2016
    Hi Tapio,
    I believe that is correct.  Mach3 should flush all its buffers and wait for all motion to complete before calling the Macro that notifies the Plugin.
    I think it would be simpler and faster to only use the Coordinated motion technique only for the Threading.   Then use simple (overlapped) independent motions to do the motion back.  Like this:
    openbuf
    VM = pitch
    while (!CheckDoneBuf()) ; // wait for thread pass to finish
    Move(X,A);  // begin retracting in X
    while (chan[X].Dest > Xp) ;  // As soon as possible start Z
    Move(Z,B);
    while (chan[Z].Dest < Zp) ;  // When Z gets close enough start moving X
    Move(X,C);
    while (!CheckDone(X)) ;
    openbuf
    VM = pitch
    openbuf
    linear  X               // pullout
    ExecBuf
    Tapio
    Group: DynoMotion Message: 13362 From: tapiolarikka Date: 6/15/2016
    picture worth 1000 words, I'll come bak when I have some experience to share
    Thank you for help
    Tapio
    Group: DynoMotion Message: 13399 From: Tapio Larikka Date: 6/29/2016
    Attachments :
      I got through my first step of passing the parameters to user program.
      but got stuck with the GetSpindleRPS.
      Please see below code: enabling any of options 1 to 3 gives compiler error
      Any idea why? Is GetSpindleRPS not available from user program?
      Rgds,
      Tapio
      //Plugin calls for Mach3 NotifyPlugins Commands
      void Tap(void);
       int msg = persist.UserData[6];  // Mach3 notify Message 10000-10999
       printf("Mach3 Notify Call, Message = %d\n",msg);
       if (msg==10076)
        Tap();
      void Tap(void)
       //  #10  1010    18 19          XEnd
       //  #11  1011    20 21          ZEnd
       //  #12  1012    22 23          Pitch
       //  #13  1013    24 25          H = Depth of first pass
       //  #14  1014    26 27          I = Infeed Angle
       //  #15  1015    28 29          R = XStart
       //  #16  1016    30 31          K = ZStart
       //  #17  1017    32 33          C = X Clearance
       //  #18  1015    34 35          Complete Flag
       double XEnd  = *(double *)&persist.UserData[18];
       double ZEnd  = *(double *)&persist.UserData[20];
       double Pitch  = *(double *)&persist.UserData[22];
       double H   = *(double *)&persist.UserData[24];
       double I  = *(double *)&persist.UserData[26];
       double R  = *(double *)&persist.UserData[28];
       double K  = *(double *)&persist.UserData[30];
       double C  = *(double *)&persist.UserData[32];
       printf("XEnd = %f\n",XEnd);
       printf("ZEnd = %f\n",ZEnd);
       printf("Pitch = %f\n",Pitch);
       printf("Depth of first pass = %f\n",H);
       printf("I = Infeed Angle = %f\n",I);
       printf("R = XStart = %f\n",R);
       printf("K = ZStart = %f\n",K);
       printf("C = X Clearance = %f\n",C);
       //printf("S = %f\n",GetSpindleRPS);     // option 1
       //double S = GetSpindleRPS; // option 2
       //float S = GetSpindleRPS;  // option 3
       //printf("S = %f\n",S);
      Group: DynoMotion Message: 13400 From: Tom Kerekes Date: 6/29/2016
      Hi Tapio,
      The Spindle related information is in the Spindle Object as defined by the SPINDLE data structure in KMotionDef.h.  So the current speed would be printed with:
       printf("S = %f\n",Spindle.TrueSpeedRPS);
      void Tap(void);
       if (msg==10076)
        Tap();
      void Tap(void)
      Group: DynoMotion Message: 13413 From: Tapio Larikka Date: 6/30/2016
      That worked.
      I'm planning to do TrigThreaning(Spindle.TrueSpeedRPS) since Mach already has spindle running.
      Would this work or can you see some problem with this?
      Rgds
      Tapio
      Group: DynoMotion Message: 13416 From: Tom Kerekes Date: 6/30/2016
      Hi Tapio,
      I think you need to use the Theoretical Spindle Speed which the motion was planned for rather than the current speed.   Otherwise if the current speed was not exactly right there would be an error in the Thread pitch.
      I forget how your Spindle Speed Control works.  But I believe you should be able to save in a global persist variable the last desired speed setting.  Then use that.
      On 6/30/2016 12:38 PM, 'Tapio Larikka' tapio.larikka@... [DynoMotion] wrote:
      That worked.
      Rgds
      Tapio
      Group: DynoMotion Message: 14656 From: Tapio Larikka Date: 4/29/2017
      Attachments :
        I finally got forward with this threading.
        Is there any way to set up a dummy/pseudo spindle feedback?
        I would feel more secure testing/debuging this kind of codes with my spare kflop that is running open loop stepper setup
        with nothing connected to it?
        Rgds,
        Tapio
        Group: DynoMotion Message: 14658 From: Tom Kerekes Date: 4/30/2017
        Hi Tapio,
        I often simulate Spindle Feedback by configuring a Step/Dir Generator to output Quadrature to pins on JP5 and then configure the Spindle encoder input to the same pins.
        Attached is the example configuration that configures Axis 6 in that manner (set MySpindleDefs.h to use axis 6).
        Rgds,
        Tapio
        Group: DynoMotion Message: 14679 From: Tapio Larikka Date: 5/6/2017
        Attachments :
          With the feedback and a bit tinkering I now got this working in simulation, threading parameter transfer works as well as the math for flank infeed.
          As I started testing with real motions I noticed strange behavior:
          While movements both from mach jog and KMotion step response work well on all speeds with minor (<400 counts) overshoot
          on moves less than 6000counts (10000/rev).
          Strange thing is that with mach rapids ("G0X100" on MDI) the axis behaves as if there was fluctuating load, sounding similar to as if the
          timing pulley was excentric to lead screw.
          Have you heard of this kind of behaviour before?
          I the above difference makes me wonder if it is mach or PC related as (if I have understood it correctly)
          the mach jogs are more like native kflop moves in nature where as the mach commanded moves make kflop chase setpoint.
          How would I go about testing if there is jitter in setpoint stream that could cause this? Any guesses to cause are welcome.
          I'm running V4.33
          Rgds,
          Tapio
          Group: DynoMotion Message: 14680 From: TKSOFT Date: 5/6/2017
          Hi Tapio,
          I don't really understand your explanation. Fluctuating load?
          It occurs at constant speed?
          What type of system do you have? I assume Servos?
          400 counts of overshoot seems large. What is your resolution?
          You can use a C Program such as CaptureXYZMotiontoFile.c to capture the
          exact trajectory that Mach3 is creating and how it is being generated by
          KFLOP.
          On 2017-05-06 11:31, 'Tapio Larikka' tapio.larikka@...
          [DynoMotion] wrote:
          > Hi Tom,
          > flank infeed.
          > the
          > I'm running V4.33
          > Rgds,
          > Tapio
          Group: DynoMotion Message: 14681 From: Tapio Larikka Date: 5/6/2017
          I mean chancing loaed like slip stick or offcenter pulley causing the belt tension to alter.
          Yes, it occurs on constant speed.
          System is with dac driven ac servos, 10000 counts/rev, top speed set to 495000counts/sec.
          mach buffer time 3sec.
          overshoot is very small on step response graph. 400 counts is set max error and with no following error .
          I'll try to take a carefull look at the graph to figure out the actual overshoot.
          I have the max errors fairly high to compensate the difference caused by mach missing jerk control.
          I'll run the CaptureXYZ to see if there is something.
          Rgds,
          Tapio
          Group: DynoMotion Message: 14686 From: Tapio Larikka Date: 5/7/2017
          And here is the attachement
          Group: DynoMotion Message: 14687 From: Tom Kerekes Date: 5/7/2017
          Hi Tapio,
          When posting files please include a description of what they are, what code and programs were used, your interpretation, etc...
          I plotted the data.  It looks like there is some speed changing.  This was captured toward the end of a single G0?
          Please explain what you were doing and all the files so we can try to reproduce.  What Version of Mach3?
          Group: DynoMotion Message: 14690 From: Tapio Larikka Date: 5/7/2017
          The attached KFlopdata .txt is what I got with the CaptureXYZMotiotoFile.c
          Importing this to excel graph shows a jagged line whereas the same procedure with my test setup shows straight line.
          I'll try and reset mach tomorrow to see if it helps.
          Rgds,
          Tapio
          PS Big ThumbsUp for getting the G95 to KmotionCNC
          Group: DynoMotion Message: 14692 From: Tapio Larikka Date: 5/8/2017
          Attachments :
            As it was already past midnight I got triggerhappy with sending my email and forgot to attach. the below post and attachement was
            in message I sent one minute after the first with actual message.
            To make this even more confusing the first message
            appeared to group board some time after the second containing the attachement. just found delayed email notification.
            I take a short timeout to regroup my toughts and questions and get back.
            the data capture was:
            -Launched CaptureXYZMotionToFile to thread 5 from KMotion
            -entered "G0Y0" to mach MDI, starting position was 50, axis 6000steps/mm
            Rgds,
            Tapio